smile Dec 5, 2025 08:15 AM

Hello everyone,

I'd like to remotely reset an SDI12 probe connected to the fixed 12V terminal.

Do you know of a way to temporarily turn off this terminal?

I've already tried uploading a program to compile, but it didn't work.

Do you have any experience with an OS update or any other suggestions?

Many tanks

Best regards

Smile


JDavis Dec 5, 2025 04:33 PM

The constant 12V terminal is wired to have 12V as long as the data logger is supplied 12V. You need to use a SW12 channel to have program control. If you are out of SW12V channels, connect a relay to a C channel. Look at part 7321 for a solid state relay that Campbell Scientific carries. The 7321 is a 7 amp relay. Crydom makes other models as well for other current limits. Pay attention on the specification to the control voltage and control current. The C channel output 5VDC with a limited current (seen in logger specifications).